When there is a big difference between the indoor room temperature and the set temperature in heating mode, adjust the target set temperature field setting.
> Ze hebben het steeds over de target set temperature, niet over thermo off temperature(offset).
Target temperature = remote controller set temperature + 2.5c
Example: Remote controller set temperature = 20c
Target remperature = 20c + 2.5c = 22.5c
Thermo off temperature = 24.5c
Remote:
1. Press both temp down/up & Mode simultaneously.
2. Press temp up.
3. Select SU.
4. Press Mode to confirm.
5. press Temp up.
6. Select 7.
7. Press Mode to confirm.
8. Press temp up.
9. Select the value to set the desired target temperature:
0 = -2.0c
1 = -1.0c
2 = 0.0c
3 = +1.0c
4 = +2.0c
Voorbeeldje:
Target remperature = 18c + 2.5c = 20.5c
Thermo off temperature = 22.5c
Target remperature = 22c + 2.5c = 24.5c
Thermo off temperature = 26.5c
Pendelen kan gebeuren doordat de buitenunit niet verder terug kan maar ook als de binnenunit zijn eigen warmte registreert of als er luchtstroom van buiten langs de sensor gaat(rooster nabij).
Ik heb het een tijd gelogd met OpenHab die elke minuut
http://x.x.x.x/aircon/get_sensor_info gegevens opsloeg en toont in een grafiek, op die manier wist ik dat het niet zo is, er was overduidelijk te zien dat de airco werd beinvloed door zijn eigen warmte.
Gedrag van compressor + binnen & buitentemp stonden erin, als de airco aan ging zag je heel snel de "binnentemp" oplopen terwijl het in de kamer niet zo warm was, bij koelen was dit gedrag er niet.
Als je de grafieken een keer wil zien moet ik eerst kijken waar ik ze weer heb.
[