Eerst wordt er elke 10 minuten een wijziging gedaan, maar als de kamer na een uur nog te koud is, dan gaat de frequentie omhoog zie ik in de logs:
[14:26:31][W][auto_adaptive:384]: Z1 HEATING: Flow limited to 32.0°C (Min Limit), calculated_flow: 28.4
[14:26:31][D][auto_adaptive:482]: CMD: Set Dependent Heat Flow -> 32.0°C (max of Z1:32.0, Z2:0.0)
[14:36:31][D][auto_adaptive:276]: Starting auto-adaptive cycle, z2 independent: 0, has_cooling: 0
[14:36:31][D][auto_adaptive:318]: Processing Zone 1: Room=20.4, Target=21.0, Outside=13.0, Bias=0.0
[14:36:31][D][auto_adaptive:367]: Error: Current=0.6, Dead Zone=[-0.3, 0.4], LR=0.052
[14:36:31][D][auto_adaptive:376]: Z1 HEATING: calculated_flow: 28.0
[14:36:31][W][auto_adaptive:384]: Z1 HEATING: Flow limited to 32.0°C (Min Limit), calculated_flow: 28.0
[14:36:31][D][auto_adaptive:482]: CMD: Set Dependent Heat Flow -> 32.0°C (max of Z1:32.0, Z2:0.0)
[14:46:32][D][auto_adaptive:276]: Starting auto-adaptive cycle, z2 independent: 0, has_cooling: 0
[14:46:32][D][auto_adaptive:318]: Processing Zone 1: Room=20.5, Target=21.0, Outside=13.0, Bias=0.0
[14:46:32][D][auto_adaptive:367]: Error: Current=0.5, Dead Zone=[-0.2, 0.4], LR=0.050
[14:46:32][D][auto_adaptive:376]: Z1 HEATING: calculated_flow: 28.0
[14:46:32][W][auto_adaptive:384]: Z1 HEATING: Flow limited to 32.0°C (Min Limit), calculated_flow: 28.0
[14:46:32][D][auto_adaptive:482]: CMD: Set Dependent Heat Flow -> 32.0°C (max of Z1:32.0, Z2:0.0)
[14:56:31][D][auto_adaptive:276]: Starting auto-adaptive cycle, z2 independent: 0, has_cooling: 0
[14:56:31][D][auto_adaptive:318]: Processing Zone 1: Room=20.5, Target=21.0, Outside=13.0, Bias=0.0
[14:56:31][D][auto_adaptive:367]: Error: Current=0.5, Dead Zone=[-0.2, 0.4], LR=0.050
[14:56:31][D][auto_adaptive:376]: Z1 HEATING: calculated_flow: 28.0
[14:56:31][W][auto_adaptive:384]: Z1 HEATING: Flow limited to 32.0°C (Min Limit), calculated_flow: 28.0
[14:56:31][I][auto_adaptive:403]: Z1 HEATING: Room too cold (err: 0.50). Offset increased from 25.20 to 25.25
[14:56:31][D][auto_adaptive:482]: CMD: Set Dependent Heat Flow -> 32.0°C (max of Z1:32.0, Z2:0.0)
[15:02:28][D][auto_adaptive:276]: Starting auto-adaptive cycle, z2 independent: 0, has_cooling: 0
[15:02:28][D][auto_adaptive:318]: Processing Zone 1: Room=20.5, Target=21.0, Outside=13.0, Bias=0.0
[15:02:28][D][auto_adaptive:367]: Error: Current=0.5, Dead Zone=[-0.2, 0.4], LR=0.050
[15:02:28][D][auto_adaptive:376]: Z1 HEATING: calculated_flow: 28.5
[15:02:28][W][auto_adaptive:384]: Z1 HEATING: Flow limited to 32.0°C (Min Limit), calculated_flow: 28.5
[15:02:28][I][auto_adaptive:403]: Z1 HEATING: Room too cold (err: 0.50). Offset increased from 25.75 to 25.80
[15:02:28][D][auto_adaptive:482]: CMD: Set Dependent Heat Flow -> 32.0°C (max of Z1:32.0, Z2:0.0)
[15:06:31][D][auto_adaptive:276]: Starting auto-adaptive cycle, z2 independent: 0, has_cooling: 0
[15:06:31][D][auto_adaptive:318]: Processing Zone 1: Room=20.6, Target=21.0, Outside=13.0, Bias=0.0
[15:06:31][D][auto_adaptive:367]: Error: Current=0.4, Dead Zone=[-0.2, 0.3], LR=0.048
[15:06:31][D][auto_adaptive:376]: Z1 HEATING: calculated_flow: 28.6
[15:06:31][W][auto_adaptive:384]: Z1 HEATING: Flow limited to 32.0°C (Min Limit), calculated_flow: 28.6
[15:06:31][D][auto_adaptive:482]: CMD: Set Dependent Heat Flow -> 32.0°C (max of Z1:32.0, Z2:0.0)
[15:06:58][D][auto_adaptive:276]: Starting auto-adaptive cycle, z2 independent: 0, has_cooling: 0
[15:06:58][D][auto_adaptive:318]: Processing Zone 1: Room=20.6, Target=21.0, Outside=13.0, Bias=0.0
[15:06:59][D][auto_adaptive:367]: Error: Current=0.4, Dead Zone=[-0.2, 0.3], LR=0.048
[15:06:59][D][auto_adaptive:376]: Z1 HEATING: calculated_flow: 29.1
[15:06:59][W][auto_adaptive:384]: Z1 HEATING: Flow limited to 32.0°C (Min Limit), calculated_flow: 29.1
[15:06:59][I][auto_adaptive:403]: Z1 HEATING: Room too cold (err: 0.40). Offset increased from 26.30 to 26.34
[15:06:59][D][auto_adaptive:482]: CMD: Set Dependent Heat Flow -> 32.0°C (max of Z1:32.0, Z2:0.0)
[15:11:29][D][auto_adaptive:276]: Starting auto-adaptive cycle, z2 independent: 0, has_cooling: 0
[15:11:29][D][auto_adaptive:318]: Processing Zone 1: Room=20.6, Target=21.0, Outside=13.0, Bias=0.0
[15:11:29][D][auto_adaptive:367]: Error: Current=0.4, Dead Zone=[-0.2, 0.3], LR=0.048
[15:11:29][D][auto_adaptive:376]: Z1 HEATING: calculated_flow: 29.6
[15:11:29][W][auto_adaptive:384]: Z1 HEATING: Flow limited to 32.0°C (Min Limit), calculated_flow: 29.6
[15:11:29][I][auto_adaptive:403]: Z1 HEATING: Room too cold (err: 0.40). Offset increased from 26.84 to 26.89
[15:11:29][D][auto_adaptive:482]: CMD: Set Dependent Heat Flow -> 32.0°C (max of Z1:32.0, Z2:0.0)
[15:15:59][D][auto_adaptive:276]: Starting auto-adaptive cycle, z2 independent: 0, has_cooling: 0
[15:15:59][D][auto_adaptive:318]: Processing Zone 1: Room=20.6, Target=21.0, Outside=13.0, Bias=0.0
[15:15:59][D][auto_adaptive:367]: Error: Current=0.4, Dead Zone=[-0.2, 0.3], LR=0.048
[15:15:59][D][auto_adaptive:376]: Z1 HEATING: calculated_flow: 30.2
[15:15:59][W][auto_adaptive:384]: Z1 HEATING: Flow limited to 32.0°C (Min Limit), calculated_flow: 30.2
[15:15:59][I][auto_adaptive:403]: Z1 HEATING: Room too cold (err: 0.40). Offset increased from 27.39 to 27.44
[15:15:59][D][auto_adaptive:482]: CMD: Set Dependent Heat Flow -> 32.0°C (max of Z1:32.0, Z2:0.0)
[15:16:31][D][auto_adaptive:276]: Starting auto-adaptive cycle, z2 independent: 0, has_cooling: 0
[15:16:31][D][auto_adaptive:318]: Processing Zone 1: Room=20.6, Target=21.0, Outside=13.0, Bias=0.0
[15:16:31][D][auto_adaptive:367]: Error: Current=0.4, Dead Zone=[-0.2, 0.3], LR=0.048
[15:16:31][D][auto_adaptive:376]: Z1 HEATING: calculated_flow: 30.2
[15:16:31][W][auto_adaptive:384]: Z1 HEATING: Flow limited to 32.0°C (Min Limit), calculated_flow: 30.2
[15:16:31][I][auto_adaptive:403]: Z1 HEATING: Room too cold (err: 0.40). Offset increased from 27.44 to 27.49
[15:16:32][D][auto_adaptive:482]: CMD: Set Dependent Heat Flow -> 32.0°C (max of Z1:32.0, Z2:0.0)
[15:20:29][D][auto_adaptive:276]: Starting auto-adaptive cycle, z2 independent: 0, has_cooling: 0
[15:20:29][D][auto_adaptive:318]: Processing Zone 1: Room=20.6, Target=21.0, Outside=13.0, Bias=0.0
[15:20:29][D][auto_adaptive:367]: Error: Current=0.4, Dead Zone=[-0.2, 0.3], LR=0.048
[15:20:29][D][auto_adaptive:376]: Z1 HEATING: calculated_flow: 30.8
[15:20:29][W][auto_adaptive:384]: Z1 HEATING: Flow limited to 32.0°C (Min Limit), calculated_flow: 30.8
[15:20:29][I][auto_adaptive:403]: Z1 HEATING: Room too cold (err: 0.40). Offset increased from 27.99 to 28.04
[15:20:29][D][auto_adaptive:482]: CMD: Set Dependent Heat Flow -> 32.0°C (max of Z1:32.0, Z2:0.0)
[15:24:59][D][auto_adaptive:276]: Starting auto-adaptive cycle, z2 independent: 0, has_cooling: 0
[15:24:59][D][auto_adaptive:318]: Processing Zone 1: Room=20.6, Target=21.0, Outside=13.0, Bias=0.0
[15:24:59][D][auto_adaptive:367]: Error: Current=0.4, Dead Zone=[-0.2, 0.3], LR=0.048
[15:24:59][D][auto_adaptive:376]: Z1 HEATING: calculated_flow: 31.3
[15:24:59][W][auto_adaptive:384]: Z1 HEATING: Flow limited to 32.0°C (Min Limit), calculated_flow: 31.3
[15:24:59][I][auto_adaptive:403]: Z1 HEATING: Room too cold (err: 0.40). Offset increased from 28.54 to 28.58
[15:24:59][D][auto_adaptive:482]: CMD: Set Dependent Heat Flow -> 32.0°C (max of Z1:32.0, Z2:0.0)
[15:26:31][D][auto_adaptive:276]: Starting auto-adaptive cycle, z2 independent: 0, has_cooling: 0
[15:26:31][D][auto_adaptive:318]: Processing Zone 1: Room=20.6, Target=21.0, Outside=13.0, Bias=0.0
[15:26:31][D][auto_adaptive:367]: Error: Current=0.4, Dead Zone=[-0.2, 0.3], LR=0.048
[15:26:31][D][auto_adaptive:376]: Z1 HEATING: calculated_flow: 31.4
[15:26:31][W][auto_adaptive:384]: Z1 HEATING: Flow limited to 32.0°C (Min Limit), calculated_flow: 31.4
[15:26:31][I][auto_adaptive:403]: Z1 HEATING: Room too cold (err: 0.40). Offset increased from 28.58 to 28.63
[15:26:31][D][auto_adaptive:482]: CMD: Set Dependent Heat Flow -> 32.0°C (max of Z1:32.0, Z2:0.0)
[15:29:29][D][auto_adaptive:276]: Starting auto-adaptive cycle, z2 independent: 0, has_cooling: 0
[15:29:29][D][auto_adaptive:318]: Processing Zone 1: Room=20.6, Target=21.0, Outside=13.0, Bias=0.0
[15:29:29][D][auto_adaptive:367]: Error: Current=0.4, Dead Zone=[-0.2, 0.3], LR=0.048
[15:29:29][D][auto_adaptive:376]: Z1 HEATING: calculated_flow: 31.9
[15:29:29][W][auto_adaptive:384]: Z1 HEATING: Flow limited to 32.0°C (Min Limit), calculated_flow: 31.9
[15:29:29][I][auto_adaptive:403]: Z1 HEATING: Room too cold (err: 0.40). Offset increased from 29.13 to 29.18
[15:29:29][D][auto_adaptive:482]: CMD: Set Dependent Heat Flow -> 32.0°C (max of Z1:32.0, Z2:0.0)